[Tp.backoffice] Update of the snags

Mitchelson.pierre at tpmanagementsa.com Mitchelson.pierre at tpmanagementsa.com
Fri Jul 2 13:11:29 MDT 2021


Hello Mr Gerry,
There are the update of the snags , I add a the sites closed in a table for you.

ID
REQUEST
COMMENTS
STATUS
dates Resolved
HDO103
Oil sensor replacement
Oil Sensor Replaced
Close
25-Jun-21
HDC014
Starter battery, automation wiring to be done, put site on auto with grid
starter battery replaced
Close

HDC011
Action from EDH to close cut out fuse, TP team to test ATS when voltage available
ATS tested
Close

HDO565
Request for Site Cleaning
stite is clean
Close

HDO190
Request for Site Cleaning
stite is clean
Close
03-Jun-21
HDO023
Request for Site Cleaning
stite is clean
Close
04-Jun-21
HDO274
Request for Site Cleaning
stite is clean
Close
04-Jun-21
HDO234
Request for Site Cleaning
stite is clean
Close
04-Jun-21


The  whole table

Issue #
TT/WO
Site ID
Section
Action Register
Request
Owner
Date issue raised
Date issue  solved
Issue status
Job completion Digicel Supervisor Confirmation
Comments
1

HDO103
Power
Oil sensor faulty
Oil sensor replacement
Talkpool
13-May-21
25-Jun-21
Close

Oil Sensor Replaced
2

HDS115
Power
Starter battery faulty
Starter battery replacement
Talkpool
15-May-21

Pending

no starter battery at Digicel
3

HDS115
Power
Oil leakage in the front seal
Oil leakage to fix
Talkpool
15-May-21

Pending

this Problem doesn't exist on the site
4

HDS106
Power
Starter battery faulty on genset #1
Starter battery replacement
Talkpool
17-May-21

Pending

no starter battery at Digicel
5

HDS106
Power
CTRL board faulty on genset #2
CTRL board
Talkpool
17-May-21

Pending


6

HDS106
Power
Oil sensor faulty on genset #2
Oil sensor replacement
Talkpool
17-May-21

Pending


7
Carl Edouard
HDO051
Power
Front seal and back seal leaking
Front seal and back seal to be replaced
Talkpool
25-May-21

Pending

they have the spares but they didn't isntalled them yet
8
Innocent Lucson
HDC012
Power
Fuel leakage on main tank partially fixed, radiator still leaks, ATS & Tank not tighten on concrete.
Replace Radiator, ATS & Tank to fix
Talkpool
09-Jun-21

Pending

radiater replaced (jun 21)
9

HDO581
Power
ATS load connection wrong, automation wiring missing, Grid counter & safety not fixed
Tighten counter & safety to grid pole, Correct ATS connection, add genset wiring automation
Talkpool
11-Jun-21

Pending


10
Innocent Lucson
HDC014
Power
Starter battery missing, Automation wiring cable not connected, Grid switch OFF.
Starter battery, automation wiring to be done, put site on auto with grid
Talkpool
29-Apr-21

Close

starter battery replaced
11

HDC014
Power
Starter battery added, automation wiring done, Grid switch OFF.
Request from Talkpool team in the area to put Grid switch on when voltage available
Talkpool
29-Apr-21

Pending


12

HDC011
Power
Grid Cut Out fuse open, ATS to swap/repair, illegal connection.
Action from EDH to close cut out fuse, TP team to test ATS when voltage available
Talkpool
08-Jun-21

Close

ATS tested
13

HDC006
Power
Genset oil leakage, Huawei cabinet risky connection, padlock key not found on site.
TP team to solve oil leakage on genset and test ATS when voltage available, add wiring automation
Talkpool
09-Jun-21

Pending


14

HDO083
Power
Site is not auto due faulty ATS (ATS contactor burnt)
ATS to fix or replace
Talkpool
14-Jun-21

Pending


15

HDO083
Power
Inside of the  shelter the air conditioners are not working
A/C unit to be fixed
Talkpool
14-Jun-21

Pending


16

HDO083
Power
Only genset running on site and the second is out of service and water pump is suspected faulty
The second genset needs to be fixed asap (Important Hubsite)
Talkpool
14-Jun-21

Pending


17

HDO083
Power
One of the AC throws a lot of water on the batteries.
The air conditioner must be repaired immediately to prevent electronic equipment from coming into contact with water.
Talkpool
14-Jun-21

Pending


18

HDN158
Power
Oil leakage in the block engine, Back seal and the Crank case.
Corrective for oil leakage
Talkpool
14-Jun-21

Pending


19

HDN158
Power
Radiator dirty
Clean the radiator
Talkpool
14-Jun-21

Pending


20

HDN158
Power
Genset needs maintenance
Maintenance to make in the E-Power
Talkpool
14-Jun-21

Pending


21

HDN158
Power
Genset very dirty
Genset to clean
Talkpool
14-Jun-21

Pending


22

HDO231
Power
Oil leak at the level of the rear seal and under the cylinder head,
Oil leak to fix
Talkpool
04-Jun-21

Pending


23

HDO231
Power
Return current observed when HPU is running on battery
Issue to fixed
Talkpool
04-Jun-21

Pending


24

HDO063
Power
Transformer and counter broken,
Replace the counter and transformer
Digicel
10-Jun-21

Pending


25

HDO060
Power
Main dropout breaker missing
Replace the dropoutbreaker
Digicel
10-Jun-21

Pending


26

HDO070
Power
wire burnt in the transformer, drop out breaker open
deep instigation to find te root cause of opening breaker
Talkpool
09-Jun-21

Pending


27

HDO679
Power
Segment of AC cable missing from the main breaker to the  Huawei cabinet
Replace the missing AC cable and put the site in auto mode with grid source
Talkpool
09-Jun-21

Pending


28

HDO003
Power
illegal connection, genset canopy and environment dirty
Remove the illegation connection and clean site environment
Talkpool
07-Jun-21

Pending


29

HDO408
Power
Major oil leak at the level of the rear seal,
Fix the seal issue and clean environment,
Talkpool
12-Jun-21

Pending


30

HDO408
Power
Murphy kit is unplugging
Murphy Kit connection  to be fixed
Talkpool
12-Jun-21

Pending


31

HDO408
Power
Grounding system stolen,
Grounding cable stolen to be replaced
Talkpool
12-Jun-21

Pending


32

HDO408
Power
Drop voltage from e.Power to cabinet 2v
Drop voltage to be fixed while changing the welding cable
Talkpool
12-Jun-21

Pending


33

HDO408
Power
Radiator very dirty and untighten,
Fix and clean radiator,
Talkpool
12-Jun-21

Pending


34

HDO408
Power
Environment is like a forest
Site environment to be cleaned
Talkpool
12-Jun-21

Pending


35

HDO565
Power
Site perimeter has a lot of Unwanted Plants
Request for Site Cleaning
Talkpool
20-May-21

Close
Yes
stite is clean
36

HDO565
Power
Site Perimeter Cyclone Fence is broken/Fall
Needed to replace the Cyclone Fence
Talkpool
20-May-21

Close
Yes
stite is clean
37

HDO190
Power
Site perimeter has a lot of Unwanted Plants
Request for Site Cleaning
Talkpool
30-May-21
03-Jun-21
Close
Yes
stite is clean
38

HDO651
Power
Front/Seal and back seal oil leak
Seal Replacement
Talkpool
01-Jun-21

Pending


39

HDO023
Power
Site perimeter has a lot of Unwanted Plants
Request for Site Cleaning
Talkpool
01-Jun-21
04-Jun-21
Close
Yes
stite is clean
40

HDO274
Power
Site perimeter has a lot of Unwanted Plants
Request for Site Cleaning
Talkpool
01-Jun-21
04-Jun-21
Close

stite is clean
41

HDO523
Power
Site perimeter has a lot of Unwanted Plants and Trash infront of the Site
Request for Site Cleaning
Talkpool
10-Jun-21

Pending


42

HDO523
Power
Site Perimeter Cyclone Fence is broken/Fall
Needed to replace the Cyclone Fence
Talkpool
10-Jun-21

Pending


43

HDO234
Power
Site perimeter has a lot of Unwanted Plants
Request for Site Cleaning
Talkpool
10-Jun-21
04-Jun-21
Close

stite is clean
44

HDO234
Power
Site Perimeter Cyclone Fence is broken/Fall
Needed to replace the Cyclone Fence
Talkpool
10-Jun-21

Pending


45

HDO164
Power
Front/Seal and back seal oil leak
Seal Replacement
Talkpool
16-Jun-21

Pending


46

HDO671
Power
Site perimeter has a lot of Unwanted Plants
Request for Site Cleaning
Talkpool
16-Jun-21

Pending


47

HDO244
Power
Site perimeter has a lot of Unwanted Plants
Request for Site Cleaning
Talkpool
16-Jun-21

Pending