For the fuel Lines, please add the following:
1. For Hybrid gensets where Ascot/E-Power is installed:
* Verify if the Fuel lines are and Tanks are still connected or available at site.
* This will be removed by the plumbing team as part of the clean up.
2. For CPS sites and Normal Gensets
* Check if the clear hose is secured with Cage and with the Padlock.
* Check if the Tank is closed with the padlock.
* Check that the Fuel tank is not rusted.
* Check that the Fuel Line Piping are good, or if required replacement.
* Check that the Fuel Hose lines are good or recommend to replace with the Galvanize pipes.
* Check if there are extra Fuel Lines (used before by the second genset) that needs to be removed as the site is working with single genset now.
* Add the other points specified in your mail below.
Thanks.
BR
Gerry
From: Moustafa Fouad <moustafa.fouad at talkpool.com>
Sent: 29 April 2021 10:51
To: tp.backoffice at tpmanagementsa.com; jean.jacques at tpmanagementsa.com; bernst.nestor at tpmanagementsa.com; eliphene.peterson at tpmanagementsa.com
Cc: Gerry Bolante <gerry.bolante at talkpool.com>; Bernard Yacoub <bernard.yacoub at talkpool.com>
Subject: 1st training with PMBO instructions
Dear Jacky , all
Please find below Points discussed today , Kindly send your QA report and snags by emails to supervisors
PM
follow Up PM done per day, and report data to planner , and reasons why not done
WFM-BO
consumable
daily calculation of consumables filters frequency , to communicate with Tech. who carried wrong PM frequency , to record all comments in quality report
WFM-BO
verify all filters replaced during PM are new , and date of PM marked on filters
WFM-BO
Maintenance
starter battery , DC alternator ( measurement values to be add in QA ) to follow up DW -acids add on starter battery or not ( add comments and call the tech.) , cleaning of Starter battery , tighten of terminals
WFM-BO
Radiator maintenance inside until it show qualified coolant color & outside by blower to be checked and observed in WFM
WFM-BO
genset body clean up from dirt , dust , grease , oil ...etc.
WFM-BO
check fuel Hose quality , to indicate clean level of fuel
WFM-BO
to verify if there is leak in fuel line or decanter and report on quality report
WFM-BO
verify decanter condition to be changed
WFM-BO
verify if there is Junk consumables on site left from the tech.
WFM-BO
verify Murphy Kit availability in EPOWER , ASCOT sites
WFM-BO
ensure murphy kit empty from Old Oil ,before carry new PM
WFM-BO
verify hybrid batteries are cleaned by Blower , and photo to be inserted in WFM
WFM-BO
Top up DW for Hybrid batteries and measure. The level before and after is necessary
WFM-BO
control panel brand , ATS brand to be add in QA report ( and if found faulty to be submit by email as major snag )
WFM-BO
Thanks
Moustafa Fouad
Network performance service manager
74 Rue Gregoire Ville de Pétion-Ville, Haiti, Haiti
www.talkpool.com<http://www.talkpool.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://tpmanagementsa.com/pipermail/tp.backoffice_tpmanagementsa.com/attachments/20210429/4a32f237/attachment-0001.html>
More information about the Tp.backoffice
mailing list